Hi I've been trying to communicate with a Micrologix 1100 but I cant get the BOOTP Software to recognize the controller. Anyone had this problem before. I have tried turning off the controller and trying again but still wouldnt see it. Brand new controller.
Guest
2020-04-29T17:39:04Z
I had the same problem recently. I finally quit trying to get the BOOTP to work and established communications with the PLC serially. From there I was able to setup the TCP/IP comm properties and was able to communcate via ethernet.
joenew
  •  joenew
  • 52.59481% (Neutral)
  • Newbie Topic Starter
2020-04-29T17:40:01Z
Thanks that worked for me also
tcox13
2020-04-29T17:41:13Z
Since this thread is 15 months old, this may not help the original posters, but might be of use to someone at a later time.

I also had problems getting the Rockwell BOOTP server to talk to my Micrologix PLC. I found that BOOTP acted like a one shot. It worked fine on a fresh boot of my laptop PC. Once the connection to the PLC was severed, it did not work a 2nd time without rebooting the laptop. I don't know why this occurred. Everything else about the laptop Ethernet port looked healthy. So next time, try running BOOTP off a fresh boot of XP Pro.