Hello,

What function does the "Watch Dog" timer provide ? How can it be used in troubleshooting problems (if applicable).

I have a SLC 5/03 Using RSLogix 500

Thank You,

K-
Guest
2020-04-29T16:39:03Z
A watchdog timer is a timer that is used to make sure some unexpected problem does not keep the system processing as it should. There are several of them in the SLC and they are common to every PLC that I know. In the most common sense (and probably what you are referring to), there is a watchdog timer that covers the processor scan. If the scan takes too long to complete due to a poorly written loop or jump routine, the watchdog timer will expire and fault out the PLC. This is a major fault and is only recoverable by clearing the fault, fixing the problem, and starting the PLC back up. It's primary purpose is to prevent the PLC from going into LaLa land (technical term) due to a programming error. You generally will not have a problem with this error. You can change the watchdog timer period in the case that you have a massive program that needs a long time to process. Generally that means you have the wrong processor for the job - need more power. With the SLC there are also hardware watchdogs that look for unexected hardware issues, STI watchdog, and the program scan watchdog that I have explained.
klm
  •  klm
  • 70.75848% (Friendly)
  • Advanced Member Topic Starter
2020-04-29T16:39:50Z


I appreciate your help in explaining this -



Thank you,

klm
RSLogix500 Introduction
RSLogix500 Inserting Instructions
RSLogix500 Opening a File
RSLogix500 Creating a Project
RSLogix500 Instruction Comments
RSLogix500 Rung Comments Page Titles
RSLogix500 Inserting Branches
RSLogix500 Program Organization, Part 1 - Overview
RSLogix500 Program Organization, Part 2 - Examples
RSLogix500 Using Symbols
RSLogix500 View Properties
RSLinx
RSLogix500 Online Offline
RSLogix500 Dowloading and Uploading
RSLogix500 Processor Modes
RSLogix500 Processor and Cards
RSLogix500 Introduction to Faults
RSLogix500 Indirect Addressing
RSLogix500 Indirect Addressing Faults
RSLogix500 Handling Faults
RSLogix500 Forcing I/O
RSLogix500  Custom Data Monitor
RSLogix500 I/O Configuration
RSLogix500 Advanced Diagnostics
RSLogix500 Instructions OTL OTU, Part 1
RSLogix500 Instructions OTL OTU, Part 2
RSLogix500 Instructions OTL OTU, Part 3
RSLogix500 Instructions, OTE
RSLogix500 Instructions, XIC XIO
RSLogix500 Instructions, ADD
RSLogix500 Instructions, COP
RSLogix500 Instructions, CPT - Part 2
RSLogix500 Instructions, CTU CTD - Part 1
RSLogix500 Instructions, CTU CTD - Part 2
RSLogix500 Instructions, CTU CTD - Part 3
RSLogix500 Instructions, CPT - Part 1
RSLogix500 - Comparison - Part1
RSLogix500 - Comparison - Part 2
RSLogix500 Instructions, DIV
RSLogix500 - FIFO - FFL and FFU - Part 1
RSLogix500 - FIFO - FFL and FFU - Part 2
RSLogix500 Instructions, FLL
RSLogix500 Instructions, JMP and LBL
RSLogix500 Instructions, Masking and MEQ
RSLogix500 Instructions, MUL
RSLogix500 Instructions, MOV
RSLogix500 Instructions, LIM
RSLogix500 Instructions, NEG
RSLogix500 Instructions, OSR
RSLogix500 Instructions, RTO
RSLogix500 Instructions, SQO sequencer - Part 1 of 3
RSLogix500 Instructions, SQO sequencer - Part 2 of 3
RSLogix500 Instructions, SQO sequencer - Part 3 of 3
RSLogix500 Instructions, SUB
RSLogix500 Instructions, TOF
RSLogix500 Instructions, JSR and RET
RSLogix500 Shift registers
RSLogix500 Instructions, SQR
RSLogix500 Instructions, TON - Part 1
RSLogix500 Instructions, TON - Part 2
RSLogix500 Instructions, TON - Part 3
Introduction to Ladder Logic