pinkerton
2020-04-29T22:46:23Z
Hello,

What is the difference between DH+ and Remote IO?

I'd like to know 1756-DHRIO can support both protocols. I plan to do new communication between new machine (CompactLogix L32E) with machines(SLC5/04) by converting EtherNet to Remote IO with Prolinx (5210-DFNT-RIO). Does is it possible? Please suggestion
Guest
2020-04-29T22:46:59Z
Good question. It's always interesting when you have to connect the newer products with the older stuff. First the difference between RIO and DH+. Simply, DH+ is a communications protocol that allows older SLCs and PLC5s to communicate with each other via messaging instructions. It is also the best way for the older devices to connect to HMI's and SCADA systems. Remote I/O or RIO is simply that. A protocol for getting remote rack and device (some drives and other products used this also) information into the processor. It can be used for data transfer to HMI's but it is very cumbersome used like that - dont.

The prolinx device you mention connects ethernet I/P to a RIO slave or adapter. That is very important on the RIO side because it tells you that it is not polling for information to gather but providing information to a remote system. I dont think that is what you want and I wouldnt want to use remote I/O for messaging back and forth between PLCs if it did work. I think a better device would be the prosoft AN-X-AB-DHRIO. It will allow the Ethernet I/P network devices to access the DH+ network which is what you have on the front of the SLC 5/04. You can find more here:

http://prosoft-technolog...thernet_ip/an_x_ab_dhrio 

Users browsing this topic
RSLogix500 Introduction
RSLogix500 Inserting Instructions
RSLogix500 Opening a File
RSLogix500 Creating a Project
RSLogix500 Instruction Comments
RSLogix500 Rung Comments Page Titles
RSLogix500 Inserting Branches
RSLogix500 Program Organization, Part 1 - Overview
RSLogix500 Program Organization, Part 2 - Examples
RSLogix500 Using Symbols
RSLogix500 View Properties
RSLinx
RSLogix500 Online Offline
RSLogix500 Dowloading and Uploading
RSLogix500 Processor Modes
RSLogix500 Processor and Cards
RSLogix500 Introduction to Faults
RSLogix500 Indirect Addressing
RSLogix500 Indirect Addressing Faults
RSLogix500 Handling Faults
RSLogix500 Forcing I/O
RSLogix500  Custom Data Monitor
RSLogix500 I/O Configuration
RSLogix500 Advanced Diagnostics
RSLogix500 Instructions OTL OTU, Part 1
RSLogix500 Instructions OTL OTU, Part 2
RSLogix500 Instructions OTL OTU, Part 3
RSLogix500 Instructions, OTE
RSLogix500 Instructions, XIC XIO
RSLogix500 Instructions, ADD
RSLogix500 Instructions, COP
RSLogix500 Instructions, CPT - Part 2
RSLogix500 Instructions, CTU CTD - Part 1
RSLogix500 Instructions, CTU CTD - Part 2
RSLogix500 Instructions, CTU CTD - Part 3
RSLogix500 Instructions, CPT - Part 1
RSLogix500 - Comparison - Part1
RSLogix500 - Comparison - Part 2
RSLogix500 Instructions, DIV
RSLogix500 - FIFO - FFL and FFU - Part 1
RSLogix500 - FIFO - FFL and FFU - Part 2
RSLogix500 Instructions, FLL
RSLogix500 Instructions, JMP and LBL
RSLogix500 Instructions, Masking and MEQ
RSLogix500 Instructions, MUL
RSLogix500 Instructions, MOV
RSLogix500 Instructions, LIM
RSLogix500 Instructions, NEG
RSLogix500 Instructions, OSR
RSLogix500 Instructions, RTO
RSLogix500 Instructions, SQO sequencer - Part 1 of 3
RSLogix500 Instructions, SQO sequencer - Part 2 of 3
RSLogix500 Instructions, SQO sequencer - Part 3 of 3
RSLogix500 Instructions, SUB
RSLogix500 Instructions, TOF
RSLogix500 Instructions, JSR and RET
RSLogix500 Shift registers
RSLogix500 Instructions, SQR
RSLogix500 Instructions, TON - Part 1
RSLogix500 Instructions, TON - Part 2
RSLogix500 Instructions, TON - Part 3
Introduction to Ladder Logic